Question 4010 of 243 · NICET Fire Alarm Systems Level IV

An atrium has a 90 ft ceiling and a risk of smoke stratification. Which design approach addresses this?

Exactly one answer is correct.

Show solution

Correct answer to question 4010

  • A: Detection at several heights, such as beams or ASD ports below the hot layer

Explanation

Smoke from a small fire may stop rising at a warm air layer below a high ceiling. Detectors at different levels, often projected beams or ASD sampling points, can catch smoke that never reaches the ceiling.

Next to question ›