Question 4009 of 243 · NICET Fire Alarm Systems Level IV
Where should smoke detectors be placed on a peaked ceiling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4009
- B: Within 3 ft of the peak, measured horizontally
Explanation
On peaked ceilings, a row of detectors is placed within 36 in. of the peak measured horizontally. Further detectors are spaced from there down the slope.