Question 4055 of 243 · NICET Fire Alarm Systems Level IV
How often must an ERCES be tested after acceptance under the IFC?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4055
- D: Annually, plus after any change that may affect it
Explanation
The IFC requires annual testing of ERCES and testing after modifications that may affect coverage. Signal strength, battery and booster functions are checked and documented.