Question 4001 of 243 · NICET Fire Alarm Systems Level IV

An air sampling smoke detection system is being designed for a data center. What maximum transport time from the farthest sampling port is generally permitted?

Exactly one answer is correct.

Show solution

Correct answer to question 4001

  • D: 120 seconds

Explanation

The code limits the time for smoke to travel from the most remote sampling port to the detector, commonly to 120 seconds. The design software calculates it and the acceptance test confirms it.

Next to question ›