Question 2023 of 183 · Ohio Fire Alarm Certification Exam
What does NFPA 72 require of equipment installed in a fire alarm system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2023
- C: It must be listed for the purpose for which it is used
Explanation
NFPA 72 requires equipment constructed and installed under the standard to be listed for the purpose for which it is used. Devices from different makers are allowed where they are listed as compatible.