Two wire smoke detectors are being added to an existing control unit. What must be confirmed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2024
- D: That the detectors are listed as compatible with the control unit
Explanation
Two wire smoke detectors draw power from the initiating circuit, so they must be listed as compatible with the control unit circuit. An incompatible detector may fail to signal an alarm.