A panel draws 0.5 A in standby and 3 A in alarm. Using 24 hours standby and 5 minutes alarm, what is the required capacity before any safety margin?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3003
- C: 12.25 ampere hours
Explanation
Standby is 0.5 A x 24 h = 12 Ah. Alarm is 3 A x 5/60 h = 0.25 Ah. The total is 12.25 Ah before a safety margin is applied. Forgetting to convert 5 minutes to hours is the usual mistake.
More questions: Circuits, Power Supplies and Control Units
- 3004A battery calculation gives 10 ampere hours. NFPA 72 (2022) requires an aging correction factor of 1.25. What battery capacity is needed at minimum?
- 3005A notification circuit draws 2 A and the total resistance of both conductors is 1.5 ohms. What is the voltage drop on the circuit?
- 3006Which marking does NFPA 72 require on the circuit disconnecting means for the fire alarm branch circuit?
- 3007What information about the primary power supply must be identified at the fire alarm control unit?
- 3008What describes a Class A pathway?