Ohio Fire Alarm Certification Exam, Circuits, Power Supplies and Control Units: all 30 questions
All questions from the Circuits, Power Supplies and Control Units section for Ohio Fire Alarm Certification Exam, each with the correct answer.
- 3001For a non-voice fire alarm system, what secondary power capacity does NFPA 72 require?
- 3002What alarm duration must the secondary power of an in-building emergency voice/alarm communication system support after 24 hours of standby?
- 3003A panel draws 0.5 A in standby and 3 A in alarm. Using 24 hours standby and 5 minutes alarm, what is the required capacity before any safety margin?
- 3004A battery calculation gives 10 ampere hours. NFPA 72 (2022) requires an aging correction factor of 1.25. What battery capacity is needed at minimum?
- 3005A notification circuit draws 2 A and the total resistance of both conductors is 1.5 ohms. What is the voltage drop on the circuit?
- 3006Which marking does NFPA 72 require on the circuit disconnecting means for the fire alarm branch circuit?
- 3007What information about the primary power supply must be identified at the fire alarm control unit?
- 3008What describes a Class A pathway?
- 3009Which pathway class keeps operating through a single open, a single ground fault and a wire to wire short?
- 3010An open occurs in the middle of a Class B initiating device circuit. What is the result?
- 3011What does pathway survivability Level 2 generally require?
- 3012A ground fault develops on a monitored fire alarm pathway. What must the system do?
- 3013What is the purpose of an end of line resistor on a conventional initiating device circuit?
- 3014Which article of NFPA 70 (National Electrical Code) covers the wiring of fire alarm systems?
- 3015A trouble signal is silenced at the control unit but the fault is not fixed. What must happen?
- 3016From what source must the primary power for a fire alarm system come?
- 3017A panel draws 0.25 A in standby and 1.2 A in alarm. With 24 hours standby and 5 minutes alarm, what capacity is needed before margin?
- 3018A voice system draws 1 A in standby and 4 A in alarm. With 24 hours standby and 15 minutes alarm, what capacity is needed before margin?
- 3019A notification circuit runs 500 feet out to the last appliance. The wire has 2 ohms per 1,000 feet. What is the total loop resistance?
- 3020A 24 V notification circuit has a 3 V drop. What percentage of the supply voltage is lost?
- 3021Why do notification circuit voltage drop calculations often start from 20.4 V instead of 24 V?
- 3022A 24 V notification circuit carries 2 A. How much power does it deliver?
- 3023Ten strobes on one circuit each draw 0.1 A. What is the total circuit current?
- 3024Which wiring method is not allowed on a supervised initiating device circuit?
- 3025How must the outgoing and return conductors of a Class A pathway generally be routed?
- 3026Which pathway class was added to NFPA 72 for Ethernet network infrastructure?
- 3027Under NEC Article 760, how far must power limited fire alarm cables generally be kept from electric light and power conductors?
- 3028Which power limited fire alarm cable type is listed for use in plenums?
- 3029The fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?
- 3030What is the main feature of a Class C pathway?