A battery calculation gives 10 ampere hours. NFPA 72 (2022) requires an aging correction factor of 1.25. What battery capacity is needed at minimum?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3004
- D: 12.5 ampere hours
Explanation
Applying the 1.25 aging correction factor means multiplying by 1.25: 10 Ah x 1.25 = 12.5 Ah. The older 20 percent margin (12 Ah) was replaced in the 2022 edition. The next larger standard battery size is then selected.