A panel draws 0.25 A in standby and 1.2 A in alarm. With 24 hours standby and 5 minutes alarm, what capacity is needed before margin?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3017
- D: 6.1 ampere hours
Explanation
Standby is 0.25 A x 24 h = 6 Ah. Alarm is 1.2 A x 5/60 h = 0.1 Ah. The total is 6.1 Ah before a safety margin is added.