Why do notification circuit voltage drop calculations often start from 20.4 V instead of 24 V?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3021
- C: It is the battery voltage near the end of its rated discharge
Explanation
A 24 V lead acid battery set falls to about 20.4 V (85 percent) at the end of its standby and alarm duty. Designing from this value makes sure appliances still get their listed minimum voltage on battery power.