Question 4006 of 183 · Ohio Fire Alarm Certification Exam
How does NFPA 72 relate the temperature rating of a fixed temperature heat detector to the ceiling temperature?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4006
- A: The rating must be at least 20 degrees F above the maximum expected ceiling temperature
Explanation
NFPA 72 requires heat detectors to have a rating at least 20 degrees F above the maximum expected ambient ceiling temperature to avoid unwanted alarms.