A fixed temperature heat detector is rated at 200 degrees F. Which classification and color code apply?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4007
- B: Intermediate, white
Explanation
NFPA 72 classifies 175 to 249 degrees F as intermediate with a white color code. Ordinary is 135 to 174 degrees F (uncolored), and high is 250 to 324 degrees F (blue).