Above what ceiling height does NFPA 72 require heat detector spacing to be reduced?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4008
- D: Above 10 feet
Explanation
NFPA 72 provides spacing reduction factors for spot type heat detectors on ceilings higher than 10 ft, because heat dilutes as it rises in a tall space.
More questions: Initiating Devices
- 4009At what height must the operable part of a manual fire alarm box be mounted?
- 4010Where must a manual fire alarm box be located relative to an exit door?
- 4011What is the maximum horizontal travel distance on the same floor to the nearest manual fire alarm box?
- 4012Within what time must a waterflow switch produce an alarm signal after flow equal to the smallest sprinkler starts?
- 4013A valve supervisory switch on an OS&Y valve must signal by what point of valve operation?
- 4014May duct smoke detectors be used in place of open area smoke detection?