A valve supervisory switch on an OS&Y valve must signal by what point of valve operation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4013
- B: Within two revolutions of the handwheel or one fifth of the travel
Explanation
NFPA 72 requires the supervisory signal within two revolutions of the handwheel or when the valve has moved one fifth of its travel distance, and the signal must not restore until the valve is fully open again.