Why do vane type waterflow switches usually have an adjustable retard?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4025
- C: To prevent false alarms from pressure surges in the piping
Explanation
Short pressure surges in the water supply can move the vane briefly. The retard delays the signal so that only sustained flow causes an alarm, while still meeting the 90 second limit.