When should smoke detectors be installed in a building under construction?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4027
- A: After construction cleanup is finished, unless they are needed and protected
Explanation
NFPA 72 says smoke detectors should not be installed until final cleaning is done, because construction dust contaminates them. If detection is required during construction, the detectors must be protected and then cleaned or replaced.
More questions: Initiating Devices
- 4001Spot type smoke detectors on a smooth flat ceiling have no listed spacing. What nominal spacing does NFPA 72 permit?
- 4002Using a 30 foot nominal spacing for smoke detectors, every point on the ceiling must be within what distance of a detector?
- 4003A spot type smoke detector is mounted on a sidewall. Where must the top of the detector be?
- 4004A heat detector has a listed spacing of 50 feet. What is the maximum distance from the detector to a wall?
- 4005On a peaked ceiling, where must a row of spot type detectors be placed relative to the peak?
- 4006How does NFPA 72 relate the temperature rating of a fixed temperature heat detector to the ceiling temperature?