Exits are grouped in an opening wider than 40 feet. Where must manual fire alarm boxes be placed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4026
- A: Within 5 feet of each side of the opening
Explanation
Where grouped openings exceed 40 ft in width, NFPA 72 requires manual fire alarm boxes within 5 ft of each side of the grouped openings.