How often must spot type smoke detectors be functionally tested under NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6001
- D: Annually
Explanation
The NFPA 72 test frequency table calls for an annual functional test of smoke detectors, using a method from the manufacturer such as listed aerosol or smoke.