Question 6008 of 183 · Ohio Fire Alarm Certification Exam
How is a non restorable fixed temperature heat detector tested in the field?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6008
- D: Mechanically and electrically, without applying heat
Explanation
Applying heat would destroy a non restorable element, so NFPA 72 calls for a mechanical and electrical functional test instead. Long term reliability is covered by the 15 year replacement or lab sample rule.