Question 6009 of 183 · Ohio Fire Alarm Certification Exam
How often must manual fire alarm boxes be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6009
- D: Annually
Explanation
The NFPA 72 test frequency table calls for annual functional testing of manual fire alarm boxes.
More questions: Inspection, Testing and Maintenance
- 6010How often must audible and visible notification appliances be tested under NFPA 72?
- 6011How often must sprinkler waterflow alarm devices connected to the fire alarm system be tested?
- 6012After a software change, which devices must be tested in a reacceptance test?
- 6013What marking does NFPA 72 require on batteries used for fire alarm secondary power?
- 6014How often must the control equipment of a fire alarm system that is monitored for alarm, supervisory and trouble signals be visually inspected?
- 6015How many devices must be tested during the initial acceptance test of a new fire alarm system?