After a software change, which devices must be tested in a reacceptance test?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6012
- D: All functions affected plus 10 percent of unaffected initiating devices
Explanation
For site specific software changes NFPA 72 requires testing of all functions known to be affected and 10 percent of initiating devices not directly affected (at least 1, up to 50).