What must be verified when testing a duct smoke detector with sampling tubes?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6017
- C: That the airflow pressure difference is within the listed range
Explanation
Duct detectors rely on air flowing through the sampling tubes. NFPA 72 requires testing to confirm that the pressure differential or airflow is within the manufacturer's listed range, in addition to the functional test.