Why is a magnet test alone not enough for a functional test of a smoke detector?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6016
- A: It does not prove that smoke can enter the sensing chamber
Explanation
The functional test must confirm that smoke can actually reach the sensing chamber and produce an alarm, so NFPA 72 calls for smoke or a listed aerosol as the manufacturer directs. A magnet only tests the electronics.