Question 4016 of 153 · Oklahoma Fire Alarm Technician Exam

What is the minimum conductor size permitted in a multiconductor power limited fire alarm cable?

Exactly one answer is correct.

Show solution

Correct answer to question 4016

  • D: 26 AWG

Explanation

Multiconductor PLFA cable may have conductors as small as 26 AWG. Single conductors must be at least 18 AWG. The actual size is chosen from voltage drop and the manufacturer's requirements.

Next to question ›