What is the minimum conductor size permitted in a multiconductor power limited fire alarm cable?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4016
- D: 26 AWG
Explanation
Multiconductor PLFA cable may have conductors as small as 26 AWG. Single conductors must be at least 18 AWG. The actual size is chosen from voltage drop and the manufacturer's requirements.