What is the main purpose of the equipment grounding conductor connected to a fire alarm control unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4017
- C: To give fault current a low impedance path
Explanation
The equipment grounding conductor bonds metal parts to ground and provides an effective fault current path, so a fault opens the breaker instead of leaving the enclosure energized.
More questions: Installation, Wiring and Pathways
- 4018Which NEC section requires electrical equipment to be installed in a neat and workmanlike manner?
- 4019According to Article 90, what is the purpose of the NEC?
- 4020Fire alarm cable passes through a 1 hour fire rated wall. What must be done with the opening?
- 4021What does the NEC require for accessible portions of abandoned fire alarm cable?
- 4022What is the maximum conduit fill for three or more conductors in a raceway?
- 4023A shielded cable is used for a signaling line circuit. How should the drain or shield normally be connected?