Question 4031 of 153 · Oklahoma Fire Alarm Technician Exam
Where is the end of line resistor installed on a Class B notification appliance circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4031
- B: After the last appliance
Explanation
The end of line device goes at the far end, after the last appliance, so supervision current passes through all the wiring. Installing it at the panel leaves the field wiring unsupervised.
More questions: Installation, Wiring and Pathways
- 4032How must EMT be supported in relation to outlet boxes?
- 4033Where must splices in fire alarm conductors be made?
- 4034A cable runs through holes bored in wood studs. When must a steel plate protect it?
- 4035Non power limited fire alarm (NPLFA) circuits must be installed using which wiring methods?
- 4001Why should smoke detectors generally not be installed until after construction cleanup is complete?
- 4002What distinguishes a Class A pathway from a Class B pathway?