A cable runs through holes bored in wood studs. When must a steel plate protect it?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4034
- D: When the edge of the hole is less than 1 1/4 in from the face of the stud
Explanation
Bored holes must be at least 1 1/4 in from the nearest edge of the framing member, or a steel plate at least 1/16 in thick protects the cable from nails and screws.