Question 5012 of 153 · Oklahoma Fire Alarm Technician Exam
What is the frequency for the visual inspection of fire alarm control units in a monitored system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5012
- A: Annually
Explanation
For control units that are monitored for alarm, supervisory and trouble signals, the visual inspection interval is annual. Unmonitored control units require more frequent inspection.
More questions: Inspection, Testing and Service
- 5013How often must a sealed lead acid fire alarm battery receive its load voltage and charger tests?
- 5014During an annual test, a duct smoke detector does not alarm with test smoke. What should the technician check first?
- 5015What is the required frequency for testing a vane type waterflow switch with flow through the inspector's test connection?
- 5016During an acceptance test, which items should the technician verify for every notification appliance?
- 5017Which personnel qualification does NFPA 72 accept for inspection, testing and maintenance of fire alarm systems?
- 5018A detector repeatedly causes nuisance alarms near a kitchen entrance. What is the most appropriate corrective action?