How often must a sealed lead acid fire alarm battery receive its load voltage and charger tests?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5013
- D: Semiannually
Explanation
Valve regulated lead acid batteries are inspected and tested semiannually, including the charger test and the discharge or load voltage test.