Which personnel qualification does NFPA 72 accept for inspection, testing and maintenance of fire alarm systems?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5017
- C: Factory training and certification, NICET certification, or a state or local license
Explanation
NFPA 72 recognizes qualification through manufacturer training, nationally recognized certification such as NICET, or licensing by a state or local authority, plus documentation of qualifications.
More questions: Inspection, Testing and Service
- 5018A detector repeatedly causes nuisance alarms near a kitchen entrance. What is the most appropriate corrective action?
- 5019How often must manual fire alarm boxes be functionally tested?
- 5020How often must audible and visible notification appliances be functionally tested?
- 5021During the annual test of a monitored system, what must be verified with the supervising station?
- 5022A smoke detector shows a dirty or maintenance alert. What is the correct service approach?
- 5023A Class B initiating circuit with a 4.7 kilohm end of line resistor is disconnected from the panel and measured. The meter shows OL (infinite). What does this indicate?