A heat detector listed for 50 ft spacing is installed on a smooth 15 ft high ceiling. Using the NFPA 72 high ceiling reduction factor of 0.77 for 14 to 16 ft, what is the adjusted spacing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1007
- B: 38.5 ft
Explanation
Above 10 ft the listed spacing of heat detectors is reduced. For a ceiling between 14 ft and 16 ft the multiplier is 0.77: 50 ft x 0.77 = 38.5 ft. Using the full 50 ft would leave the hot gas layer too far from the detector at that height.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1008The highest expected ceiling temperature in a mechanical room is 120 F. What is the lowest fixed-temperature heat detector rating that may be used?
- 1009A fixed-temperature heat detector is rated 194 F. In which NFPA 72 temperature classification does it fall?
- 1010What color marking identifies a heat detector in the intermediate temperature classification?
- 1011The general contractor asks you to install the smoke detectors while drywall sanding is still going on, and nobody has required detection for protection during construction. What should you do?
- 1012Smoke detectors were installed early to protect a building during construction. What must happen to them before the system is accepted?
- 1013After installing a new smoke detector you notice the plastic dust cover is still on it. When must the cover come off?