Question 1008 of 299 · NICET Fire Alarm Systems Level I
The highest expected ceiling temperature in a mechanical room is 120 F. What is the lowest fixed-temperature heat detector rating that may be used?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1008
- B: 140 F
Explanation
The temperature rating of a fixed-temperature heat detector must be at least 20 F above the maximum expected ceiling temperature: 120 F + 20 F = 140 F. A lower rating invites nuisance alarms on hot days.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1009A fixed-temperature heat detector is rated 194 F. In which NFPA 72 temperature classification does it fall?
- 1010What color marking identifies a heat detector in the intermediate temperature classification?
- 1011The general contractor asks you to install the smoke detectors while drywall sanding is still going on, and nobody has required detection for protection during construction. What should you do?
- 1012Smoke detectors were installed early to protect a building during construction. What must happen to them before the system is accepted?
- 1013After installing a new smoke detector you notice the plastic dust cover is still on it. When must the cover come off?
- 1014Under which ambient condition may a spot-type smoke detector NOT be installed unless it is specifically listed for that condition?