Question 1050 of 299 · NICET Fire Alarm Systems Level I
When must a valve supervisory (tamper) switch send its off-normal signal?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1050
- B: Within two turns of the handwheel or one fifth of the stem travel
Explanation
The supervisory signal must start during the first two revolutions of the handwheel or when the stem has moved one fifth of its travel from normal. Waiting for a fully closed valve would let someone partially close the valve without notice.