Question 1051 of 299 · NICET Fire Alarm Systems Level I
A ceiling is peaked, with slopes rising to a ridge. Where is the first row of spot-type smoke detectors placed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1051
- C: Within 36 in. of the peak, measured horizontally
Explanation
Smoke and heat rise to the peak, so on a peaked ceiling a row of detectors is located within 36 in. of the peak, measured horizontally. Additional detectors are then spaced out from there.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1052Which article of the National Electrical Code covers fire alarm system wiring?
- 1053A power-limited fire alarm cable will be run through a ceiling space used for environmental air (a plenum). Which cable type is required?
- 1054A power-limited fire alarm cable runs vertically through a shaft from floor to floor. Which cable type is the minimum rating suitable for this riser?
- 1055Your shop has no FPLR on the truck. Which cable may be substituted for FPLR in a riser application?
- 1056Which cable may be used in place of FPLP in a plenum?
- 1057What does the letter group NPLF on a fire alarm cable jacket indicate?