Before touching conductors you have de-energized, you test them with a voltage tester. What else must you do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1117
- B: Check the tester on a known live source before and after the test
Explanation
OSHA requires the test instrument to be checked for proper operation immediately before and after the test, so a dead meter cannot give a false no-voltage reading.