Question 2079 of 299 · NICET Fire Alarm Systems Level I

The panel and its outputs will be tested, but the owner does not want the sprinkler pump or door holders to operate. What is the right approach?

Exactly one answer is correct.

Show solution

Correct answer to question 2079

  • C: Bypass only as agreed, and test those functions later or document why not

Explanation

Functions that are not tested must be documented, not reported as passing. Bypass only what was agreed, restore it afterward and record anything left untested.