The panel and its outputs will be tested, but the owner does not want the sprinkler pump or door holders to operate. What is the right approach?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2079
- C: Bypass only as agreed, and test those functions later or document why not
Explanation
Functions that are not tested must be documented, not reported as passing. Bypass only what was agreed, restore it afterward and record anything left untested.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2080How often must a digital alarm communicator transmitter (DACT) send an automatic test signal to the supervising station?
- 2081Which maintenance task applies to vented lead-acid batteries but not to sealed VRLA batteries?
- 2082When battery terminals show white or green corrosion, what should the technician do?
- 2083On a two-wire conventional zone, the panel shows a trouble when one detector head is removed. Is this normal?
- 2084A strobe circuit shows a trouble at the panel. Which first check makes the most sense?
- 2085With all strobes on, the voltage at the last strobe of a NAC measures 15.5 V, and the strobes are listed for 16 to 33 V. What is the problem?