NICET Fire Alarm Systems Level I, Maintenance (Periodic Testing, Repair and Replacement): all 134 questions
All questions from the Maintenance (Periodic Testing, Repair and Replacement) section for NICET Fire Alarm Systems Level I, each with the correct answer.
- 2001How often must spot-type smoke detectors receive a functional test?
- 2002When is the first sensitivity test of newly installed smoke detectors required?
- 2003After the first sensitivity test, how often are smoke detector sensitivity tests normally repeated?
- 2004Two consecutive sensitivity tests show a group of smoke detectors stayed within their listed range. What is the maximum interval the tests may then be extended to?
- 2005Which method may NOT be used to measure smoke detector sensitivity?
- 2006What does a proper annual functional test of a spot-type smoke detector have to prove?
- 2007How is a restorable spot-type fixed-temperature heat detector functionally tested?
- 2008Why is a heat test not done on a nonrestorable fixed-temperature heat detector?
- 2009Nonrestorable spot-type fixed-temperature heat detectors have been in service for 15 years. What is required?
- 2010A building has 300 nonrestorable spot-type heat detectors that are 15 years old. The owner chooses lab testing instead of replacement. How many detectors must be sent for testing?
- 2011How often are manual fire alarm boxes functionally tested?
- 2012How often are audible and visible notification appliances functionally tested?
- 2013How often must sprinkler waterflow alarm devices connected to the fire alarm system be tested?
- 2014How often must valve supervisory (tamper) switches be tested?
- 2015A waterflow switch is tested by opening the inspector's test valve. What flow is the test meant to simulate?
- 2016During a tamper switch test you close the valve. When should the supervisory signal clear?
- 2017Before starting a test that will activate initiating devices, who must be notified?
- 2018You have finished testing a building and restored the system. What notification is required at the end?
- 2019Who is responsible for making sure a fire alarm system is inspected, tested and maintained?
- 2020How long must inspection and test records be kept?
- 2022After a new device is installed on an existing system, what testing is required?
- 2023The site-specific software of a control unit was changed. Besides the functions known to be affected, how many other initiating devices must be tested?
- 2024What is the purpose of the 100 percent acceptance test on a new fire alarm system?
- 2025At acceptance testing, how are installation conductors checked for unwanted voltages?
- 2026To measure loop resistance of an initiating device circuit during acceptance testing, what is done at the far end of the circuit?
- 2027A technician checks fire alarm conductors for isolation from ground. What is being looked for?
- 2028You need to megger (insulation resistance test) a new fire alarm circuit. What must be done first?
- 2029When measuring the voltage on a notification appliance circuit with a multimeter, how is the meter connected?
- 2030When measuring current drawn by a strobe circuit with a multimeter, how is the meter connected?
- 2031Why must resistance measurements be made with the circuit de-energized?
- 2032You disconnect a Class B initiating device circuit at the panel and measure across the pair. The meter shows about 4,700 ohm, matching the EOL value. What does this tell you?
- 2033Measured across a disconnected Class B circuit pair, the meter shows OL (over limit). What is the most likely problem?
- 2034Across a disconnected initiating circuit pair, the meter reads close to 0 ohm. What is the most likely problem?
- 2035A panel shows a ground fault. Which technique is commonly used to locate it on a long circuit?
- 2036What sound level meter weighting is used to measure fire alarm audibility?
- 2037At what height above the floor are audibility measurements normally taken?
- 2038The average ambient sound level in a store is 62 dBA. What minimum fire alarm sound level is needed for public mode, if no louder short-term noise is present?
- 2039In a factory, the average ambient is 70 dBA but a machine produces 88 dBA for several minutes at a time. What minimum public mode sound level is needed?
- 2040In a private mode signaling area, such as a nurses station, how far above the average ambient must the signal be?
- 2041In sleeping areas, what minimum sound level is required at the pillow, besides the 15 dB over ambient rule?
- 2042Which audible signal frequency is required for alarm signals that awaken sleeping occupants in sleeping areas where required by NFPA 72?
- 2043What is the maximum sound pressure level allowed for audible fire alarm signals?
- 2044Two horns each produce 80 dBA at a measuring point. What is the combined level at that point?
- 2045A horn measures 90 dBA at 10 ft in a free field. What level would you expect at 20 ft?
- 2046What pattern does the standard evacuation signal (temporal-3) use?
- 2047For a fire alarm system that is not a voice system, what secondary power capacity does NFPA 72 require?
- 2048For an in-building emergency voice/alarm communications system, how long must the batteries run the system in alarm after 24 hours of standby?
- 2049A panel draws 0.25 A in standby and 2.0 A in alarm. Using 24 hours standby, 5 minutes alarm and the 1.25 aging correction factor required by NFPA 72 (2022/2025), what battery capacity is needed?
- 2050A small panel draws 0.150 A in standby and 1.2 A in alarm. Without a safety factor, what is the required battery capacity for 24 hours standby plus 5 minutes alarm?
- 2051How must storage batteries for a fire alarm system be marked?
- 2052During the annual test, a sealed lead-acid battery cannot hold its voltage under load and falls below the manufacturer's limit. What should be done?
- 2053Two batteries in series supply a 24 V panel. One battery fails its test. What is good practice?
- 2054To test the transfer to secondary power, the technician switches off the AC branch circuit. What should happen?
- 2055On a control unit, what is the difference between silencing and resetting?
- 2056What signal type does a fire alarm panel use to report a fault in the system, such as an open circuit?
- 2057A sprinkler control valve has been closed. What type of signal should the panel show?
- 2058During an inspection you see the panel's trouble LED lit and the buzzer was silenced last week. What should you do?
- 2059How often is a visual inspection of control equipment required on a system that is monitored for alarm, supervisory and trouble signals by a supervising station?
- 2060During a visual inspection of smoke detectors, what are you mainly looking for?
- 2061You find a smoke detector that was painted over during a renovation. What is the correct action?
- 2062A new office wall was built and now a smoke detector sits less than a foot from it, inside a small closet created by the wall. What should the technician do?
- 2063A smoke detector head needs to be replaced. Which replacement is acceptable?
- 2064You replace an addressable smoke detector. What must you make sure of before leaving?
- 2065A 15 cd strobe in a room designed for 30 cd has failed. What should it be replaced with?
- 2066A technician finds that a previous service person removed a detector and twisted the wires together to clear a trouble. What should be done?
- 2067A smoke detector reports a maintenance (dirty) alert at the panel. What should be done?
- 2068What is the purpose of drift compensation in a smoke detector?
- 2069An area of a building is having repeated smoke detector nuisance alarms after construction work. What is a likely cause?
- 2070How is a rate-of-rise heat detector correctly tested?
- 2071When testing a duct smoke detector, what else must be checked besides the alarm response to smoke?
- 2072What should happen when a duct smoke detector that controls air movement goes into alarm during a test?
- 2073How is a manual fire alarm box normally tested?
- 2074During the annual test of a horn/strobe circuit, what should the technician verify?
- 2075Sound level measurements of notification appliances are required by NFPA 72 mainly at which tests?
- 2076A sound level meter used for fire alarm audibility tests should meet which instrument class?
- 2077Which tool is used to deliver test aerosol to a ceiling smoke detector from the floor?
- 2078Before testing, a technician puts some zones in test or disable mode. What must be done at the end of the job?
- 2079The panel and its outputs will be tested, but the owner does not want the sprinkler pump or door holders to operate. What is the right approach?
- 2080How often must a digital alarm communicator transmitter (DACT) send an automatic test signal to the supervising station?
- 2081Which maintenance task applies to vented lead-acid batteries but not to sealed VRLA batteries?
- 2082When battery terminals show white or green corrosion, what should the technician do?
- 2083On a two-wire conventional zone, the panel shows a trouble when one detector head is removed. Is this normal?
- 2084A strobe circuit shows a trouble at the panel. Which first check makes the most sense?
- 2085With all strobes on, the voltage at the last strobe of a NAC measures 15.5 V, and the strobes are listed for 16 to 33 V. What is the problem?
- 2086During testing a horn sounds weak and distorted. The other horns on the circuit are normal. What is the most likely cause?
- 2087A waterflow alarm comes in every time the city water pressure surges, without any real flow. What adjustment is most likely needed?
- 2088What is the reason for testing carbon monoxide detectors per their manufacturer's instructions instead of with smoke aerosol?
- 2089A household smoke alarm in an apartment was manufactured 11 years ago. What should be done?
- 2090During acceptance testing of a Class A initiating circuit, how is the redundant path proven?
- 2091How is ground fault supervision of a circuit verified during acceptance testing?
- 2092Within what time must a battery charger be able to recharge fully discharged fire alarm batteries?
- 2093A smoke detector is marked with a listed sensitivity range of 1.0 to 3.5 percent per foot obscuration. The test reads 3.9 percent per foot. What does this mean?
- 2094An addressable panel prints sensitivity readings for every smoke detector. May this be used for the required sensitivity test?
- 2095What qualification does NFPA 72 expect from people who inspect, test and maintain fire alarm systems?
- 2096Which statement about a Level I trainee performing tests is true?
- 2097A device fails its annual test and cannot be fixed the same day. What should the technician do?
- 2098What is the difference between a deficiency and an impairment in NFPA 72 terms?
- 2099Which records must stay with the system for its entire life, rather than only for a test cycle?
- 2100What is positive alarm sequence (PAS)?
- 2101Under positive alarm sequence, how quickly must trained staff acknowledge the alarm at the control unit?
- 2102When a fire alarm system activates door hold-open releases during testing, what should the technician verify?
- 2103An elevator lobby smoke detector is activated during testing. What should the elevators do?
- 2104A projected beam smoke detector needs its annual functional test. Which method is acceptable?
- 2105When cleaning a spot-type smoke detector, what should guide the method?
- 2106What is the main purpose of the panel lamp test function?
- 2107During testing, the panel shows an alarm, but the supervising station reports it received a trouble. What does this indicate?
- 2108A pressure-type waterflow switch is used on a dry pipe sprinkler system. What does it sense?
- 2109On a dry pipe sprinkler system, which condition sends a supervisory signal, not an alarm?
- 2110The ambient sound in a hotel room is 40 dBA. What minimum alarm level is needed at the pillow?
- 2111Which pattern identifies a carbon monoxide alarm signal?
- 2112What should the panel do when a single conventional smoke detector circuit goes into alarm and alarm verification is enabled?
- 2113What does a supervising station do with signals from a protected building?
- 2114After a fire alarm technician finishes a repair to field wiring, what testing is needed?
- 2115Which tool is best for measuring the current drawn by a NAC without opening the circuit?
- 2116A NAC carries 1.8 A in alarm and the voltage at the panel is 24 V. The total wire resistance out and back is 2.0 ohm. What voltage reaches the end of the circuit?
- 2117An initiating device circuit has a 3,900 ohm EOL resistor and 24 V across it. What supervisory current flows in normal standby, ignoring the detectors?
- 2118With all appliances operating, the current on a strobe circuit is measured at 2.9 A. The NAC is rated 2.5 A. What should be done?
- 2119What should the technician check when inspecting a remote annunciator?
- 2120The inspection report must be provided to whom after a test?
- 2121Which information belongs in an inspection and test record?
- 2122A smoke detector in a hallway is about 30 years old. It still passes its functional and sensitivity tests. What is generally true?
- 2123A heat detector of the line type (linear heat cable) is the nonrestorable kind. How is its annual test done?
- 2124During a visual inspection, you find storage stacked within a few inches of a ceiling heat detector. What is the concern?
- 2125Why should a technician wait for the smoke to clear a detector before resetting the panel during a test?
- 2126When a fire alarm system will be out of service for repair, what interim measure might the owner have to provide?
- 2127What is the main reason to notify the supervising station before testing?
- 2128During an annual test, a technician activates a smoke detector, and the panel shows the alarm but no horns sound. Which check comes first?
- 2129How should replacement fuses in a fire alarm panel be chosen?
- 2130What is the normal state of the panel's AC power indicator in standby?
- 2131When inspecting a strobe in a room, the lens is cracked but the strobe still flashes. What should be done?
- 2132Why are batteries disconnected last when powering down a panel for service and connected after AC when powering up, in many manufacturers' instructions?
- 2133A technician must measure the resistance of an initiating circuit. What must be done first?
- 2134Before an insulation resistance (megger) test on field wiring, what must be disconnected?
- 2135After a fire alarm test is finished, which step completes the job on site?