On a two-wire conventional zone, the panel shows a trouble when one detector head is removed. Is this normal?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2083
- A: Yes, removing a head should open the circuit and cause a trouble
Explanation
Detector removal must be supervised, so pulling a head on a conventional zone opens the circuit and shows a trouble. If no trouble appears, check the wiring and EOL location.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2084A strobe circuit shows a trouble at the panel. Which first check makes the most sense?
- 2085With all strobes on, the voltage at the last strobe of a NAC measures 15.5 V, and the strobes are listed for 16 to 33 V. What is the problem?
- 2086During testing a horn sounds weak and distorted. The other horns on the circuit are normal. What is the most likely cause?
- 2087A waterflow alarm comes in every time the city water pressure surges, without any real flow. What adjustment is most likely needed?
- 2088What is the reason for testing carbon monoxide detectors per their manufacturer's instructions instead of with smoke aerosol?
- 2089A household smoke alarm in an apartment was manufactured 11 years ago. What should be done?