On a two-wire conventional zone, the panel shows a trouble when one detector head is removed. Is this normal?

Exactly one answer is correct.

Show solution

Correct answer to question 2083

  • A: Yes, removing a head should open the circuit and cause a trouble

Explanation

Detector removal must be supervised, so pulling a head on a conventional zone opens the circuit and shows a trouble. If no trouble appears, check the wiring and EOL location.