What is positive alarm sequence (PAS)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2100
- D: A staffed delay that lets trained staff check an automatic detector alarm first
Explanation
With PAS, trained staff must acknowledge a signal from an automatic detector within 15 seconds and then have up to 180 seconds to investigate before the general alarm sounds. Manual boxes and second detectors bypass the delay.