Question 2104 of 299 · NICET Fire Alarm Systems Level I

A projected beam smoke detector needs its annual functional test. Which method is acceptable?

Exactly one answer is correct.

Show solution

Correct answer to question 2104

  • A: The manufacturer's method, such as a listed test filter

Explanation

Beam detectors are tested by the method in their listing, commonly a calibrated filter that reduces the beam a known amount. A full block gives a trouble, not a proper alarm test.

Next to question ›