Question 2116 of 299 · NICET Fire Alarm Systems Level I
A NAC carries 1.8 A in alarm and the voltage at the panel is 24 V. The total wire resistance out and back is 2.0 ohm. What voltage reaches the end of the circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2116
- B: 20.4 V
Explanation
Voltage drop = I x R = 1.8 A x 2.0 ohm = 3.6 V. End voltage = 24 V - 3.6 V = 20.4 V.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2117An initiating device circuit has a 3,900 ohm EOL resistor and 24 V across it. What supervisory current flows in normal standby, ignoring the detectors?
- 2118With all appliances operating, the current on a strobe circuit is measured at 2.9 A. The NAC is rated 2.5 A. What should be done?
- 2119What should the technician check when inspecting a remote annunciator?
- 2120The inspection report must be provided to whom after a test?
- 2121Which information belongs in an inspection and test record?
- 2122A smoke detector in a hallway is about 30 years old. It still passes its functional and sensitivity tests. What is generally true?