With all appliances operating, the current on a strobe circuit is measured at 2.9 A. The NAC is rated 2.5 A. What should be done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2118
- A: Move some appliances to another circuit or power supply
Explanation
The circuit exceeds its rating, so the panel may shut down the NAC or appliances may not get enough voltage. Split the load to another NAC or booster power supply.