Question 2123 of 299 · NICET Fire Alarm Systems Level I
A heat detector of the line type (linear heat cable) is the nonrestorable kind. How is its annual test done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2123
- C: Test it mechanically and electrically, without a heat test
Explanation
Heating nonrestorable linear heat cable would destroy that section. The test checks the cable mechanically and electrically for function and continuity per the manufacturer.