Question 2006 of 172 · Texas Fire Alarm License Exam
Six strobes each draw 0.12 A and four horn/strobes each draw 0.16 A on one NAC. The total alarm current is
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2006
- A: 1.36 A
Explanation
6 x 0.12 A = 0.72 A plus 4 x 0.16 A = 0.64 A, for a total of 1.36 A.