- 2001For a protected premises fire alarm system, NFPA 72 requires secondary power capable of operating the system in quiescent load for
- 2002A fire alarm panel draws 0.45 A in standby and 2.8 A in alarm. Using 24 hours standby, 5 minutes alarm and the 20 percent safety margin required by NFPA 72 (2019), the minimum battery is about
- 2003An emergency voice/alarm communications system requires secondary power for 24 hours standby followed by how many minutes of alarm at maximum connected load?
- 2004A notification appliance circuit carries 1.5 A to the last appliance 400 ft from the panel on 14 AWG solid copper (about 3.07 ohms per 1,000 ft). The approximate voltage drop is
- 2005A 24 VDC initiating device circuit ends in a 4,700 ohm end-of-line resistor. The supervisory current through the resistor is about
- 2006Six strobes each draw 0.12 A and four horn/strobes each draw 0.16 A on one NAC. The total alarm current is
- 2007For public mode audible signaling, the evacuation signal should exceed the average ambient sound level by at least
- 2008A room has an average ambient sound level of 62 dBA. Under the public mode rule based on average ambient, the minimum audible signal level is
- 2009For private mode audible signaling, the signal must be at least how many dB above the average ambient sound level?
- 2010The total sound pressure level produced by audible notification appliances, measured at the minimum hearing distance, must not exceed
- 2011Audible appliances intended to awaken occupants in sleeping areas must produce a signal of at least 15 dB above average ambient, 5 dB above the maximum 60-second level, or
- 2012Audible appliances provided for sleeping areas to awaken occupants must produce a low-frequency signal with a fundamental frequency of
- 2013The standard audible emergency evacuation signal is the
- 2014In the three-pulse temporal pattern, each cycle consists of three 0.5-second on phases separated by 0.5-second off phases, followed by
- 2015Wall-mounted visible notification appliances must be installed so the entire lens is between
- 2016The flash rate of visible notification appliances must be
- 2017When more than two visible notification appliances are in any field of view, they must
- 2018In a sleeping room, a wall-mounted visible appliance with the top of its lens less than 24 inches below the ceiling must have a minimum rating of
- 2019On a smooth ceiling, spot-type smoke detectors are permitted a nominal spacing of
- 2020A spot-type smoke detector mounted on a sidewall must be located
- 2021Spot-type heat detectors on a smooth ceiling must be located so that all points on the ceiling are within what distance of a detector?
- 2022A heat detector has a listed spacing of 50 ft. On a smooth flat ceiling, the maximum distance from the detector to a wall is
- 2023Spot-type heat detectors mounted on a sidewall must be located
- 2024For ceilings higher than 10 feet, the listed spacing of spot-type heat detectors must be
- 2025NFPA 72 guidance on placing spot-type smoke detectors says to keep them out of direct airflow and at least how far from an air supply diffuser or return opening?
- 2026Duct smoke detectors used for HVAC control
- 2027Under the adopted NFPA 90A, smoke detectors in the supply air system are required downstream of filters and ahead of branch connections in air distribution systems over
- 2028The operable part of a manual fire alarm box must be mounted
- 2029Manual fire alarm boxes must be located within 5 feet of each exit doorway on each floor, and the travel distance to the nearest box must not exceed
- 2030How often must spot-type smoke detectors receive a functional test after acceptance?
- 2031Smoke detector sensitivity must be checked within one year after installation and then
- 2032Sprinkler waterflow alarm-initiating devices and valve supervisory switches are tested at what frequency under NFPA 72?
- 2033When performing the functional test of a smoke detector, the technician should
- 2034After a modification to an existing system, reacceptance testing must include all affected devices plus
- 2035Nonrestorable fixed-temperature spot-type heat detectors that have been in service for 15 years must be
- 2036Under NFPA 72, records of inspection, testing and maintenance must be kept
- 2037A circuit that keeps operating to all devices after a single open, and also after a single ground fault or wire-to-wire short, is classified as
- 2038A Class B initiating device circuit with a single open conductor will
- 2039Pathway survivability Level 2 is generally provided by
- 2040At the control unit, an alarm signal from an initiating device must cause notification appliances to activate within
- 2041Sprinkler waterflow alarm-initiating devices must initiate an alarm signal within how long after flow equal to a single sprinkler of the smallest orifice?
- 2042Heat detectors used to initiate elevator shunt trip must be located
- 2043A central station must retransmit a fire alarm signal to the communications center within
- 2044Under NFPA 70 Article 760, the branch circuit disconnecting means for fire alarm equipment must be
- 2045Which cable type is required for power-limited fire alarm circuits installed in a plenum without a raceway?
- 2046Power-limited fire alarm circuit conductors may NOT be placed in the same raceway with
- 2047How often are restorable spot-type heat detectors functionally tested after acceptance?
- 2048A nonrestorable fixed-temperature spot-type heat detector is tested in service by
- 2049A projected beam smoke detector is functionally tested by
- 2050Where alarm verification is used for smoke detectors, the verification feature must not delay the reporting of an alarm by more than
- 2051Under positive alarm sequence, trained staff must acknowledge the alarm signal within
- 2052On a peaked ceiling, a row of spot-type smoke detectors must be located on or near the peak, within what horizontal distance of the peak?
- 2053Which smoke detector type generally responds faster to slow, smoldering fires that produce large visible particles?
- 2054Ionization smoke detectors are generally most responsive to
- 2055A rate-of-rise heat detector typically operates when the temperature rises faster than about
- 2056Under the heat detector temperature classification table, an intermediate classification detector (175 to 249 degrees F) carries what color code?
- 2057The temperature rating of a fixed-temperature heat detector must be at least how much above the maximum expected ambient ceiling temperature?
- 2058Unless the AHJ permits otherwise, manual fire alarm boxes must be
- 2059A double-action manual fire alarm box requires the user to
- 2060A single open in a Class B notification appliance circuit causes
- 2061A conventional (non-addressable) initiating device circuit in normal condition reads a wire-to-wire short at the panel as
- 2062A wire-to-wire short on a supervised notification appliance circuit normally causes
- 2063Polarized notification appliances on a supervised NAC allow the control unit to
- 2064A panel shows a ground fault trouble. A common first step to locate it is to
- 2065With an IDC disconnected from the panel, an ohmmeter across the loop reads infinite resistance. This indicates
- 2066Disconnected from the panel, a healthy Class B IDC with a 4.7 kilohm EOL resistor should read approximately
- 2067To measure the current drawn by a notification appliance circuit with a standard multimeter, the meter must be connected
- 2068Under Article 760, which cable type may be used as a substitute for type FPLR riser cable?
- 2069Article 760 requires exposed fire alarm cables to be
- 2070The branch circuit supplying fire alarm equipment must NOT be
- 2071For NPLFA circuits, 18 AWG conductors must have overcurrent protection not exceeding
- 2072The minimum conductor size permitted for non-power-limited fire alarm circuits in a multiconductor cable is
- 2073When fire alarm cables pass through a fire-rated wall, the penetration must be
- 2074Circuit integrity (CI) cable is designed to
- 2075During an acceptance test of a new fire alarm system, the share of devices and circuits that must be tested is
- 2076Smoke detectors in elevator lobbies used for elevator recall are intended to
- 2077If the elevator lobby detector on the designated recall level activates, the cars recall to
- 2078Activation of a detector in the elevator machine room or hoistway must also cause
- 2079Where a duct smoke detector is connected to a fire alarm system and area detection is present, its activation generally initiates
- 2080A valve supervisory switch must signal off-normal within two revolutions of the handwheel or when the valve stem moves
- 2081Supervisory signals at the control unit must be
- 2082A digital alarm communicator transmitter (DACT) must send a test signal to the receiver at least
- 2083A DACT must be connected to
- 2084The main difference between a smoke alarm and a smoke detector is that a smoke alarm
- 2085Fire alarm system batteries must be marked with
- 2086Primary power for a protected premises fire alarm system is generally supplied by
- 2087The location of the fire alarm branch circuit disconnecting means must be
- 2088A listed relay or control module used for an emergency control function must be located within what distance of the controlled component?
- 2089After acceptance of a new system, the document that summarizes the system and its testing is the