Texas Fire Alarm License Exam: all 172 questions with answers
Each question leads to its own page with the answers and the solution.
- Texas Fire Alarm Law and Rules83 questions
- Texas Technician Technical Knowledge (NFPA 72-2019)89 questions
Texas Fire Alarm Law and Rules
- 1001Under Texas law, an individual or organization that plans, sells, installs, services or monitors fire alarm systems as a business must first hold
- 1002Each separate office location of a registered fire alarm firm, other than the location shown on its certificate, generally needs
- 1003Before a fire alarm registration certificate is issued, the applicant must file evidence of
- 1004Unless changed by commissioner rule, the minimum general liability limits for a registered fire alarm firm are
- 1005Each registered firm, including a single station firm, must employ at least one
- 1006To lawfully perform licensed fire alarm work in Texas, a licensee must also be
- 1007Which statement about the scope of Texas fire alarm licenses is correct?
- 1008A residential fire alarm technician may provide direct on-site supervision to a registered firm's employee
- 1009Which license authorizes installing, certifying, inspecting and servicing, but NOT planning, fire alarm systems in one- and two-family residences?
- 1010Which license is limited to single station smoke or heat detectors that are not connected to any other device or system in one- and two-family homes?
- 1011Which license allows planning fire alarm systems in commercial buildings?
- 1012An applicant for a fire alarm planning superintendent license must show technical qualification by
- 1013An applicant for a fire alarm technician license may substitute for the SFMO technical qualifying test
- 1014An applicant for a residential fire alarm technician license must provide proof of
- 1015The residential fire alarm technician training course must include at least
- 1016The examination at the end of a residential fire alarm technician course must have at least 25 questions, and passing requires at least
- 1017To be approved as a fire alarm training school instructor, an applicant must hold a qualifying license and have at least
- 1018Under Chapter 6002, participation in continuing education programs for fire alarm licensees is
- 1019A renewed fire alarm license or registration certificate is valid for
- 1020A fire alarm license that has been expired for 60 days may be renewed by paying the renewal fee plus a late fee that
- 1021A fire alarm license that has been expired for two years or longer
- 1022For an individual fire alarm technician license, the initial fee and the two-year renewal fee are
- 1023A licensee whose license is unexpired but who is not employed by a registered firm at renewal time
- 1024A registration certificate or license issued under Chapter 6002
- 1025Under the fire alarm rules, a registered firm's business location must be
- 1026A registered firm's designated employee must be
- 1027A change in a firm's designated employee must be reported in writing to the State Fire Marshal's Office within
- 1028Vehicles regularly used for fire alarm installation or service must display the company name, telephone number and certificate number in letters at least
- 1029When a fire alarm firm's ownership changes completely, the firm must
- 1030How many full-time licensed individuals must a registered firm employ at each main or branch office location?
- 1031A firm applying for a registration certificate to engage in monitoring must provide evidence of
- 1032After passing a required license test, an applicant must complete all application requirements within
- 1033A licensee who renews within two years after the license expired
- 1034A licensee who changes employers or adds a registered firm must obtain a revised license by submitting written notice and the fee within
- 1035Which activity is exempt from the Texas fire alarm licensing provisions?
- 1036An electrical contractor installing fire alarm wiring and devices during construction is exempt from licensing only if, among other conditions,
- 1037A city-licensed electrician may install which devices in a residence without a fire alarm license?
- 1038Which person is exempt from the license requirement under Chapter 6002?
- 1039An employee of a registered firm who has no fire alarm license may perform installation work when
- 1040Under the fire alarm rules, the definition of direct supervision excludes the installation of
- 1041Unlicensed employees of a registered firm who sell and install single station residential alarms under the exemption must be supervised by a
- 1042A fire detection or alarm device sold or installed in Texas must generally carry
- 1043Which is a prohibited practice under Chapter 6002?
- 1044Violating the requirement to hold a firm registration certificate or a license is a
- 1045If the state fire marshal proposes to revoke a fire alarm license, the license holder is entitled to a hearing conducted by
- 1046A person whose fire alarm license was revoked may not reapply until
- 1047A Texas city or county may require a registered fire alarm firm to
- 1048A municipality may by ordinance require a registered monitoring firm to
- 1049Every fire alarm system or modification to an existing system must be planned by
- 1050Fire alarm plans, manuals and documents under the Texas rules
- 1051For a commercial installation, instead of the record of completion in the adopted standard, the licensee generally completes
- 1052A copy of a completed installation certificate must be sent to the local AHJ within
- 1053The certifying company must keep its copy of the installation certificate for
- 1054Which is one of the three required installation inspections by the licensed firm?
- 1055If corrective action from an installation inspection is not started within ten calendar days, the registered firm must
- 1056The installation label for a new fire alarm system must be
- 1057Which label must NOT be attached for the installation of a new system?
- 1058Which signature is NOT acceptable on Texas fire alarm labels?
- 1059After any service on a fire alarm system, the licensee must attach a
- 1060Service labels must remain in place for at least
- 1061What color is the Texas inspection/test label?
- 1062Inspection/test labels must remain in place for at least
- 1063For a new installation, an inspection/test label may be applied
- 1064A yellow label is attached when a system
- 1065Where must a yellow or red label be attached?
- 1066After attaching a yellow label, the licensee or firm must give written notice to the owner and the local AHJ within
- 1067A red label is attached when a system or part of it
- 1068When a red label is attached because a system is inoperable, the licensee must
- 1069When a red label is attached for a fault condition or impairment (not a fully inoperable system), written notice must be given within
- 1070During a service call a technician finds that the system did not comply with the standards adopted when it was installed. The technician must
- 1071A registered firm must keep complete records of all service, maintenance and testing on a system for at least
- 1072A Texas registered firm may monitor a fire alarm system located in Texas for
- 1073At a central station operated by a registered firm, which personnel requirement applies?
- 1074When a monitoring firm reports an alarm to a municipal emergency services center, which information must it provide at a minimum?
- 1075If monitoring service for a commercial property is discontinued before the contract ends, the monitoring firm must notify the owner and AHJ at least
- 1076Replacing a failed device in the same location with a listed, compatible device of similar characteristics, as determined by a planning superintendent, is treated as
- 1077When a building owner asks a registered firm for the system passwords, the firm
- 1078Under the Texas rules, planning and installation may follow an edition of a standard other than the edition adopted in 34.607 when
- 1079Which edition of NFPA 72 is adopted by the Texas fire alarm rules effective September 1, 2023?
- 1080If installation or service of a fire alarm system also includes work on part of a sprinkler or fire extinguisher system,
- 1081The licensee who attaches a service or inspection label must be licensed under the ACR number of
- 1082Which statement about planning and installation by different firms is correct under the Texas rules?
- 1083Before certifying a new installation, the certifying licensee of the installing firm must
Texas Technician Technical Knowledge (NFPA 72-2019)
- 2001For a protected premises fire alarm system, NFPA 72 requires secondary power capable of operating the system in quiescent load for
- 2002A fire alarm panel draws 0.45 A in standby and 2.8 A in alarm. Using 24 hours standby, 5 minutes alarm and the 20 percent safety margin required by NFPA 72 (2019), the minimum battery is about
- 2003An emergency voice/alarm communications system requires secondary power for 24 hours standby followed by how many minutes of alarm at maximum connected load?
- 2004A notification appliance circuit carries 1.5 A to the last appliance 400 ft from the panel on 14 AWG solid copper (about 3.07 ohms per 1,000 ft). The approximate voltage drop is
- 2005A 24 VDC initiating device circuit ends in a 4,700 ohm end-of-line resistor. The supervisory current through the resistor is about
- 2006Six strobes each draw 0.12 A and four horn/strobes each draw 0.16 A on one NAC. The total alarm current is
- 2007For public mode audible signaling, the evacuation signal should exceed the average ambient sound level by at least
- 2008A room has an average ambient sound level of 62 dBA. Under the public mode rule based on average ambient, the minimum audible signal level is
- 2009For private mode audible signaling, the signal must be at least how many dB above the average ambient sound level?
- 2010The total sound pressure level produced by audible notification appliances, measured at the minimum hearing distance, must not exceed
- 2011Audible appliances intended to awaken occupants in sleeping areas must produce a signal of at least 15 dB above average ambient, 5 dB above the maximum 60-second level, or
- 2012Audible appliances provided for sleeping areas to awaken occupants must produce a low-frequency signal with a fundamental frequency of
- 2013The standard audible emergency evacuation signal is the
- 2014In the three-pulse temporal pattern, each cycle consists of three 0.5-second on phases separated by 0.5-second off phases, followed by
- 2015Wall-mounted visible notification appliances must be installed so the entire lens is between
- 2016The flash rate of visible notification appliances must be
- 2017When more than two visible notification appliances are in any field of view, they must
- 2018In a sleeping room, a wall-mounted visible appliance with the top of its lens less than 24 inches below the ceiling must have a minimum rating of
- 2019On a smooth ceiling, spot-type smoke detectors are permitted a nominal spacing of
- 2020A spot-type smoke detector mounted on a sidewall must be located
- 2021Spot-type heat detectors on a smooth ceiling must be located so that all points on the ceiling are within what distance of a detector?
- 2022A heat detector has a listed spacing of 50 ft. On a smooth flat ceiling, the maximum distance from the detector to a wall is
- 2023Spot-type heat detectors mounted on a sidewall must be located
- 2024For ceilings higher than 10 feet, the listed spacing of spot-type heat detectors must be
- 2025NFPA 72 guidance on placing spot-type smoke detectors says to keep them out of direct airflow and at least how far from an air supply diffuser or return opening?
- 2026Duct smoke detectors used for HVAC control
- 2027Under the adopted NFPA 90A, smoke detectors in the supply air system are required downstream of filters and ahead of branch connections in air distribution systems over
- 2028The operable part of a manual fire alarm box must be mounted
- 2029Manual fire alarm boxes must be located within 5 feet of each exit doorway on each floor, and the travel distance to the nearest box must not exceed
- 2030How often must spot-type smoke detectors receive a functional test after acceptance?
- 2031Smoke detector sensitivity must be checked within one year after installation and then
- 2032Sprinkler waterflow alarm-initiating devices and valve supervisory switches are tested at what frequency under NFPA 72?
- 2033When performing the functional test of a smoke detector, the technician should
- 2034After a modification to an existing system, reacceptance testing must include all affected devices plus
- 2035Nonrestorable fixed-temperature spot-type heat detectors that have been in service for 15 years must be
- 2036Under NFPA 72, records of inspection, testing and maintenance must be kept
- 2037A circuit that keeps operating to all devices after a single open, and also after a single ground fault or wire-to-wire short, is classified as
- 2038A Class B initiating device circuit with a single open conductor will
- 2039Pathway survivability Level 2 is generally provided by
- 2040At the control unit, an alarm signal from an initiating device must cause notification appliances to activate within
- 2041Sprinkler waterflow alarm-initiating devices must initiate an alarm signal within how long after flow equal to a single sprinkler of the smallest orifice?
- 2042Heat detectors used to initiate elevator shunt trip must be located
- 2043A central station must retransmit a fire alarm signal to the communications center within
- 2044Under NFPA 70 Article 760, the branch circuit disconnecting means for fire alarm equipment must be
- 2045Which cable type is required for power-limited fire alarm circuits installed in a plenum without a raceway?
- 2046Power-limited fire alarm circuit conductors may NOT be placed in the same raceway with
- 2047How often are restorable spot-type heat detectors functionally tested after acceptance?
- 2048A nonrestorable fixed-temperature spot-type heat detector is tested in service by
- 2049A projected beam smoke detector is functionally tested by
- 2050Where alarm verification is used for smoke detectors, the verification feature must not delay the reporting of an alarm by more than
- 2051Under positive alarm sequence, trained staff must acknowledge the alarm signal within
- 2052On a peaked ceiling, a row of spot-type smoke detectors must be located on or near the peak, within what horizontal distance of the peak?
- 2053Which smoke detector type generally responds faster to slow, smoldering fires that produce large visible particles?
- 2054Ionization smoke detectors are generally most responsive to
- 2055A rate-of-rise heat detector typically operates when the temperature rises faster than about
- 2056Under the heat detector temperature classification table, an intermediate classification detector (175 to 249 degrees F) carries what color code?
- 2057The temperature rating of a fixed-temperature heat detector must be at least how much above the maximum expected ambient ceiling temperature?
- 2058Unless the AHJ permits otherwise, manual fire alarm boxes must be
- 2059A double-action manual fire alarm box requires the user to
- 2060A single open in a Class B notification appliance circuit causes
- 2061A conventional (non-addressable) initiating device circuit in normal condition reads a wire-to-wire short at the panel as
- 2062A wire-to-wire short on a supervised notification appliance circuit normally causes
- 2063Polarized notification appliances on a supervised NAC allow the control unit to
- 2064A panel shows a ground fault trouble. A common first step to locate it is to
- 2065With an IDC disconnected from the panel, an ohmmeter across the loop reads infinite resistance. This indicates
- 2066Disconnected from the panel, a healthy Class B IDC with a 4.7 kilohm EOL resistor should read approximately
- 2067To measure the current drawn by a notification appliance circuit with a standard multimeter, the meter must be connected
- 2068Under Article 760, which cable type may be used as a substitute for type FPLR riser cable?
- 2069Article 760 requires exposed fire alarm cables to be
- 2070The branch circuit supplying fire alarm equipment must NOT be
- 2071For NPLFA circuits, 18 AWG conductors must have overcurrent protection not exceeding
- 2072The minimum conductor size permitted for non-power-limited fire alarm circuits in a multiconductor cable is
- 2073When fire alarm cables pass through a fire-rated wall, the penetration must be
- 2074Circuit integrity (CI) cable is designed to
- 2075During an acceptance test of a new fire alarm system, the share of devices and circuits that must be tested is
- 2076Smoke detectors in elevator lobbies used for elevator recall are intended to
- 2077If the elevator lobby detector on the designated recall level activates, the cars recall to
- 2078Activation of a detector in the elevator machine room or hoistway must also cause
- 2079Where a duct smoke detector is connected to a fire alarm system and area detection is present, its activation generally initiates
- 2080A valve supervisory switch must signal off-normal within two revolutions of the handwheel or when the valve stem moves
- 2081Supervisory signals at the control unit must be
- 2082A digital alarm communicator transmitter (DACT) must send a test signal to the receiver at least
- 2083A DACT must be connected to
- 2084The main difference between a smoke alarm and a smoke detector is that a smoke alarm
- 2085Fire alarm system batteries must be marked with
- 2086Primary power for a protected premises fire alarm system is generally supplied by
- 2087The location of the fire alarm branch circuit disconnecting means must be
- 2088A listed relay or control module used for an emergency control function must be located within what distance of the controlled component?
- 2089After acceptance of a new system, the document that summarizes the system and its testing is the