A heat detector with a listed spacing of 30 ft will be installed on a 12.5 ft high ceiling. The multiplier above 12 ft up to 14 ft is 0.84. What spacing must be used?

Exactly one answer is correct.

Show solution

Correct answer to question 1057

  • C: 25.2 ft

Explanation

Adjusted spacing = 30 ft x 0.84 = 25.2 ft. Ceilings above 10 ft require reduced heat detector spacing per the code table of multipliers.