A heat detector with a listed spacing of 30 ft will be installed on a 12.5 ft high ceiling. The multiplier above 12 ft up to 14 ft is 0.84. What spacing must be used?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1057
- C: 25.2 ft
Explanation
Adjusted spacing = 30 ft x 0.84 = 25.2 ft. Ceilings above 10 ft require reduced heat detector spacing per the code table of multipliers.