Where should a sidewall mounted spot heat detector be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1058
- D: Top 4 in. to 12 in. below the ceiling
Explanation
Heat detectors may be mounted on the ceiling no closer than 4 in. to the sidewall, or on the sidewall with the top between 4 in. and 12 in. below the ceiling. The dead air space at the corner is avoided.