Question 1058 of 344 · NICET Fire Alarm Systems Level II

Where should a sidewall mounted spot heat detector be located?

Exactly one answer is correct.

Show solution

Correct answer to question 1058

  • D: Top 4 in. to 12 in. below the ceiling

Explanation

Heat detectors may be mounted on the ceiling no closer than 4 in. to the sidewall, or on the sidewall with the top between 4 in. and 12 in. below the ceiling. The dead air space at the corner is avoided.

Next to question ›