Question 1059 of 344 · NICET Fire Alarm Systems Level II
On a ceiling with solid joists, how is heat detector spacing adjusted in the direction perpendicular to the joists?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1059
- B: Reduced to 50 percent of smooth ceiling spacing
Explanation
Joists slow heat flow across the ceiling. Spacing measured at right angles to solid joists is reduced to 50 percent of the smooth ceiling spacing, while spacing parallel to the joists stays at full spacing.
More questions: Installation
- 1060What governs the spacing and mounting of projected beam smoke detectors?
- 1061Why must projected beam smoke detectors be mounted on stable surfaces?
- 1062Can a duct smoke detector be used in place of open area smoke detection?
- 1063What must be verified when installing a duct smoke detector with sampling tubes?
- 1064Where is a duct smoke detector placed on the supply side of an air handling system under NFPA 90A?
- 1065What is the mounting height range for the operable part of a manual fire alarm box?